Hi all,
I'm sorry I have to write in this forum in English, but I'm from Belgium and speak only Flemish, French and English.
I can try to read Geman replies though.
Ok can somebody please help me out here?
I have a vitodens 200 wb2 7159008...
Since a few weeks the kessel is "cycling" when put in "normal" mode (heizkring + wasser): I can hear some relais clicking, lufter starts to turn, the ionisation-led goes on for 1 sec, then it shuts down. After this it will try to start again, shutdown again, up, down, up, down, ...
It will go on like this forever.
The only way to get it up and running is to put in in mode "T2" (full power, "vollast") or in "heizwasser-only" mode (where it also gives full power).
When I put it in T2, it displays errorcodes "FE", but I don't know if those codes have been inthere already for a long time or are related to this problem.
I have measured ionisationcurrent, which is about 4 microamps on average. Strange thing is, on full power (T2 oder heizwasser-only) the ionosationcurrent is also lower than 5 micoamps.
Since the problem is occurring I can smell a strange odor, seems like rauchgas?
But to eliminate possible "rauchgas-recirculation" I run the vitodens without covers, so it just takes air from the immediate environment, and the problem keeps occuring?
hilfe bitte. Es ist kalt draussen?
I'm sorry I have to write in this forum in English, but I'm from Belgium and speak only Flemish, French and English.
I can try to read Geman replies though.
Ok can somebody please help me out here?
I have a vitodens 200 wb2 7159008...
Since a few weeks the kessel is "cycling" when put in "normal" mode (heizkring + wasser): I can hear some relais clicking, lufter starts to turn, the ionisation-led goes on for 1 sec, then it shuts down. After this it will try to start again, shutdown again, up, down, up, down, ...
It will go on like this forever.
The only way to get it up and running is to put in in mode "T2" (full power, "vollast") or in "heizwasser-only" mode (where it also gives full power).
When I put it in T2, it displays errorcodes "FE", but I don't know if those codes have been inthere already for a long time or are related to this problem.
I have measured ionisationcurrent, which is about 4 microamps on average. Strange thing is, on full power (T2 oder heizwasser-only) the ionosationcurrent is also lower than 5 micoamps.
Since the problem is occurring I can smell a strange odor, seems like rauchgas?
But to eliminate possible "rauchgas-recirculation" I run the vitodens without covers, so it just takes air from the immediate environment, and the problem keeps occuring?
hilfe bitte. Es ist kalt draussen?